Heat Pump Repair in Los Altos, CA
Let me open with something a marketing page normally leaves out. Heat pumps are not among the three equipment types that come up most on my own Los Altos service list. What I get called to here is mostly conventional split system cooling and gas furnace work. I would rather tell you that than pretend otherwise.
Here is why the page still stands up. A heat pump is a split system air conditioner that can run in reverse. The compressor, the condenser, the indoor coil, the blower and the charge are all things I work on constantly. Exactly two pieces are genuinely heat pump specific, the reversing valve and the defrost control, and those two are what most heat pump calls turn out to be about.
I am John Towner. I own Silicon Valley Comfort, I have been in this trade 25 years, I do the work myself, and the number is 408-691-5940.
Why heat pump repair in Los Altos is its own job
Los Altos has a structural reason to consider a heat pump that has nothing to do with weather. It is the Eichler blocks. Flat roof, no attic, radiant slab. There is nowhere to put a conventional attic furnace and coil, which pushes those houses toward a ducted or ductless heat pump whether anybody set out to buy one or not.
So the heat pumps here are often not a preference. They are the answer to a building that cannot take the usual equipment.
On my own records here, six jobs deep and not a survey, the brands that come up most are Bryant, ADP and Payne. Bryant and Payne share a parts family, so boards, contactors and motors cross between them, and I work as an Independent Bryant Installer, so those diagnostics are familiar ground.
The systems run from 2 tons up to 5 tons, so there is no standard machine and every number I check gets compared against the plate on your equipment.
And the only refrigerant recorded on those jobs is R-410A. That is two records out of six, so it is thin and I will not inflate it. But set next to install years running from 2014 to 2022 it points one direction. The equipment I get called to in this city is new enough that the parts are still made.
What actually fails on a Los Altos heat
Here are the three things that actually bring me out on a heat pump.
The reversing valve circuit. This is the part that makes a heat pump a heat pump. It flips the direction refrigerant travels so the same machine can cool in July and heat in January. When it will not shift you get one mode and not the other. Here is what is worth knowing before anybody quotes you a valve. The valve body itself often is not the failure. The solenoid coil that slides it is a separate piece that fails on its own, and swapping it is a fraction of the work of cutting a valve out. Anyone reaching for the valve before testing the coil has skipped a step.
The defrost control. In heating the outdoor coil is the cold side, so it collects frost. A working system periodically reverses itself, melts it off, and goes back to heating. That is why a heat pump steams outside in winter and blows cool for a couple of minutes. It is normal. What is not normal is an outdoor unit encased in ice that never clears. That is a defrost board or a defrost sensor, and left alone it will take the outdoor fan motor or the compressor with it.
Auxiliary heat running when it should not. This almost never gets reported, because nothing breaks. The heat pump quietly stops carrying the load, the electric resistance strips pick it up, the house stays warm, and your electric use climbs. If your winter usage jumped and nothing else changed, that is the first place I would look.
Conversions From Gas Furnaces
More and more Los Altos homes are replacing an old gas furnace and air conditioner with a single heat pump. In this climate it makes sense: winters are mild enough that a heat pump runs efficiently nearly every day, and it handles summer cooling with the same equipment. The catch is the ductwork. A heat pump delivers heat at a lower supply temperature than a gas furnace, so it needs more airflow to deliver the same comfort.
A lot of heat pump repair in Los Altos on newer conversions turns out to be an airflow problem, not a failed part. The system was installed on the old furnace ducts without measuring them, and the house feels lukewarm on cold mornings. Static pressure and supply temperatures tell us quickly whether the ducts can carry what the heat pump needs.
Defrost And Cold Mornings
On clear winter nights, frost forms on the outdoor coil and the heat pump runs a defrost cycle to clear it. The outdoor fan stops, the system briefly reverses, steam rolls off the coil, and heat resumes in a few minutes. During that time, the air from the vents may feel cooler. That is normal. A defrost that runs constantly, ice that builds and stays on the bottom of the coil, or a unit that never seems to come out of defrost points at a sensor, the defrost board, low refrigerant, or poor drainage under the unit.
Ductless Heads For Additions
When a Los Altos home adds a bedroom, office, or family room, extending the old duct system is often the hard way. A ductless heat pump head heats and cools the new space on its own, with a small line set and its own controls. When one of those heads stops keeping up, the cause is usually a dirty blower wheel or filter, a refrigerant issue specific to that zone, or a sensor reading the wrong temperature because the head sits in direct sun. Each head gets its supply temperature measured so the weak one stands out.
Matched Equipment And Yearly Care
When a heat pump is replaced, the outdoor unit and the indoor coil or air handler need to be a matched pair. Check that the exact combination is listed in the AHRI directory. A mismatched pair can run, but it often falls well short of its rated capacity and efficiency, and that shows up as a house that never quite feels right. A yearly check covers the outdoor coil, the reversing valve, the defrost controls, the charge in heating mode, and the electrical, with the readings saved for next time. Keep leaves and mulch away from the base of the outdoor unit so melt water from defrost can drain freely instead of freezing in place.
If the heat pump is blowing cool air on a cold morning, give it ten minutes before calling, since it may be finishing a defrost cycle. If it is still cool after that, check that the thermostat is set to heat, not cool or auto with a low setpoint, and note any error codes on the thermostat or the outdoor unit. Those few details shorten the diagnosis and usually point straight at the part.
When you book, mention whether the heat pump replaced a gas furnace and when that conversion was done. If the house has felt lukewarm since the day it was installed, that points toward airflow and setup more than a failed part, and we plan the visit around measuring the ducts as well as checking the heat pump itself. A photo of both equipment labels helps.
How I diagnose it
A heat pump diagnosis takes longer than an air conditioner diagnosis, and I would rather you know that up front.
I take superheat and subcooling in both heating and cooling modes, not one of them. A charge that reads acceptable in cooling can be wrong in heating, because the coils swap roles and the machine is not asking the same thing of the refrigerant. Checking one mode and calling it charged is how a heat pump gets left still broken.
I watch a defrost cycle actually run. Not just that the board commands one, but that it completes and terminates on the sensor rather than running out a timer. That is the difference between a system that will handle a cold snap and one that ices up the first time it gets tested.
I read supply air temperature in heating with and without auxiliary heat energized. That is the reading that catches the failure nobody notices, where the strips do the work the compressor should.
Then the ordinary things any split system needs. Compressor amp draw against the rated load amps on the plate, and static pressure across the air handler when symptoms point at airflow.
One honest limitation. If you call me in August about a heating fault, I can test a great deal of it, but I cannot force real frost onto an outdoor coil in a Los Altos summer. I will tell you plainly what I proved and what I could not.
Repair or replace
The honest case for not calling me first.
If the outdoor unit is steaming and blowing cool air for a few minutes in winter, that is a defrost cycle and the system is working correctly. If it ices over but clears itself within an hour or so, watch it before you book anything. Check the filter. Check that the thermostat is set to heat and not emergency heat, because emergency heat locks the compressor out and runs the strips on purpose.
On a ductless system the indoor head will usually blink an error code. Write the pattern down before you call. It points me at the circuit before I arrive.
Then check the original manufacturer parts warranty and whether the equipment was registered. It will not cover my labor, but it can cover a compressor or a board, and you should know before you pay anyone, me included.
On repair against replace, the install years on my Los Altos list run from 2014 to 2022 and the only refrigerant on record is R-410A. Equipment in that range still has parts in production, so a reversing valve solenoid, a defrost board, a sensor or a fan motor is normally worth doing.
What tips it the other way is a failed compressor, or a leak inside a coil that is no longer made. Ductless adds one more thing to weigh. Parts tend to come through the brand rather than a universal supplier, so a board can take longer to land, and on an older head it may not be available at all.
Los Altos neighborhoods I cover
I am not going to hand you a list of streets. Which Los Altos houses are on heat pumps is not something a map tells you, and there is a specific reason here. A lot of the housing stock has been substantially rebuilt. A house that started with a flat roof and a slab may now have a mechanical closet, a raised section or ductwork the original plan never had. What matters is what is in the building now, not what it was drawn as.
So the useful question is not which neighborhood you are in. It is these three. Is there an attic or a mechanical closet, or is the air handler tucked into something tight. Is the heat coming out of registers or up through the floor. And is it one outdoor unit feeding ducts, or one feeding wall heads in individual rooms.
Answer those on the phone and I show up with the right parts. North Los Altos, Downtown Los Altos, Country Club and the Highlands are a short drive apart for me. The drive is not the variable. The building is.
Straight Pricing, No Surprises
Residential Diagnostic
$99
Standard hours. After 6:00 PM, Saturdays, and holidays: $149. The standard diagnostic is credited toward your repair if you approve the work on the same visit.
Commercial Diagnostic
$199
Business hours. After-hours: $299. Light commercial, retail, and multi-family equipment.
Repairs and Installations
Quoted before we touch a wrench. Supplier invoice attached to your job sheet.
Heat Pump Repair Los Altos: common questions
My heat pump cools fine but will not heat. What is that?
That pattern points at the reversing valve circuit. Before anyone quotes you a valve, the solenoid coil that shifts it should be tested, because the coil fails on its own and replacing it is a much smaller job than cutting out the valve body. The other possibility is the charge is wrong, which is why I read superheat and subcooling in heating mode and not only cooling.
My outdoor unit is steaming and blowing cold air in winter. Is it broken?
Almost certainly not. That is a defrost cycle. The outdoor coil collects frost in heating, so the system briefly reverses itself to melt it, which produces steam outside and a few minutes of cool air inside. It should end on its own and go back to heating. What is not normal is a unit locked in ice that never clears.
Why did my electric use jump this winter when nothing else changed?
The usual answer is auxiliary heat strips carrying load the compressor should be carrying. Nothing breaks, so nothing gets reported, and the house stays warm while the strips run. I check it by reading supply air temperature in heating with the strips energized and with them locked out. Also make sure the thermostat is not sitting on emergency heat.
Do you work on ductless mini splits in Los Altos?
Yes, and they come up here because the Eichler blocks have flat roofs, no attic and a radiant slab, which pushes those houses toward ducted or ductless heat pumps. When you call, read me the error code the indoor head is blinking. That code narrows the circuit before I get there.
Can you diagnose a heating fault in the middle of summer?
Partly, and I will be straight about which part. I can verify the reversing valve shifts, read the charge in both modes, check amp draw, and confirm the defrost board is commanding a cycle. What I cannot do in a Los Altos summer is create real frost on the outdoor coil to prove the defrost sensor terminates properly. I will tell you what I proved and what I did not.
Is a heat pump installed around 2016 worth repairing?
Usually yes. Everything on my Los Altos list falls between 2014 and 2022, and the only refrigerant on those records is R-410A, which is still available. Boards, sensors, solenoid coils and fan motors for that generation are still made. The answer flips if the compressor is dead, or if the leak is inside a coil that is no longer made.